Diesel heaters

Reply
Created by southace > 9 months ago, 30 Apr 2020
southace
SA, 4776 posts
10 Jun 2020 5:22PM
Thumbs Up

Select to expand quote
2bish said..

southace said..


2bish said..
You've inspired me Southace (along with the 3c temp on the boat on Sunday night), I've ordered one! Did you buy extra ducting, if so from where? I'm yet to properly map out my install, but I'll likely need three outlets and upwards of 7 meters of ducting. There are plenty of options out of China, but they all have delivery times in the multiple weeks.




Ebay, ducting it was from a caravan shop I think, I ordered 3 meters. I only have one duct coming from the lazzerete under the quarter cabin bunk and jetting directly out of that cabin into the main saloon.
I would suggest buy the unit first . Set it up and dummy run it with 3 meters of duct first. I just layed the duct across the bunk for the first couple of nights before I planed to start cutting 82 mm holes in bulkheads.

fuel tank in engine room with fuel pump. (Fuel pump is most noise you will hear). I have brought a fuel transfer pump to Decan direct from my main fuel tank line into the heater Day tank.

S/S exuast hose and transom skin fitting ordered from Tasmania supplier.

I have run mine for 100 hrs since install. Using 10 litres per 45 hour runs. Last night was min. 2.5 C on deck cabin remained at 20C through out the night.

Best item I ever brought for a boat. !

enjoy!



Yeah I hear what you're saying about cutting holes in bulkheads, I want to be absolutely certain too. So good advice there! I'll look at finding the right mounting location for the heater first, get it mounted and working and plan the rest from there. I'm leaning towards using the bunnings 100mm ducting from the unit through to the salon. Then I'll reduce to 75mm through to the vee berth.
yes I'll order the skin fitting from dieselheat in Tas too.
My fuel tank is under the galley sink and has a spare pick up on it. So I'll probably mount the fuel pump in there somewhere and suspend + sound insulate it.
what did you end up doing with the muffler?


No muffler better strait out the transom. Trust me put the fuel pump in a fully soundproof locker! The 75 mm is standard on the unit I would try to avoid the Bunnings stuff but may be ok. I fired my unit up while motoring this arvo this is what you will expect to see at start up. Don't panic it does that at some starts.


Lazzz
NSW, 885 posts
10 Jun 2020 9:07PM
Thumbs Up

Select to expand quote
2bish said..
Where are you sourcing your ducting Lazzz? I see buntings has the 100mm semi flexible aluminum stuff. Maybe that's the way I should go as it's relatively cheap, easily available and will aid airflow down the length of the boat.


I ended up with this from eBay: www.ebay.com.au/itm/HyFlo-4-Inch-100mm-Double-Walled-Hydroponics-Ducting-Ventilation-Extraction/262733553814?ssPageName=STRK%3AMEBIDX%3AIT&_trksid=p2060353.m2749.l2649

Haven't actually seen the Bunnings stuff but probably OK.

I've only had it going once at full bore but seems OK - it did't melt!!

southace
SA, 4776 posts
10 Jun 2020 9:08PM
Thumbs Up

Select to expand quote
Lazzz said..

2bish said..
Where are you sourcing your ducting Lazzz? I see buntings has the 100mm semi flexible aluminum stuff. Maybe that's the way I should go as it's relatively cheap, easily available and will aid airflow down the length of the boat.



I ended up with this from eBay: www.ebay.com.au/itm/HyFlo-4-Inch-100mm-Double-Walled-Hydroponics-Ducting-Ventilation-Extraction/262733553814?ssPageName=STRK%3AMEBIDX%3AIT&_trksid=p2060353.m2749.l2649

Haven't actually seen the Bunnings stuff but probably OK.

I've only had it going once at full bore but seems OK - it did't melt!!


Gee my 3 meters cost me $170 bucks. No wonder breaking bad is so popular!

2bish
TAS, 815 posts
10 Jun 2020 9:58PM
Thumbs Up

Good one Lazzz, I'll check that out. I had a look and feel of the Bunnings stuff today. I think it's good and strong enough, a half meter length expands to 3 meters, I put a 90 degree bend into it easily and the inside radius of the bend was around 70mm. I'll wrap insulate it with something during the installation.

Very smooth interior wall too, so I guess that helps airflow.

$29 for 3 meters: www.bunnings.com.au/pacific-air-3m-x-100mm-semi-rigid-duct_p4700420

Lazzz
NSW, 885 posts
11 Jun 2020 8:51AM
Thumbs Up

Select to expand quote


I've found no sound transfer & I don't really hear much at all.
My heater, pump & tank are hidden away at the transom (short exhaust run) with about 2.5 mts of 100mm duct to a straight run of 90mm PVC pipe and then the first Y piece with a 1 mtr run and a 2.5 mtr run to the vents.

southace
SA, 4776 posts
15 Jun 2020 6:39PM
Thumbs Up

Fuel transfer pump fittted yesterday. Will transfer 5litres per minute to fill the heater 10litre tank from my main 300litre tank. Can also fill Jerry cans if I come across some twit that's run out of diesel. It's so much easier set up like this although I do need to remember to through jerrys into the main tank!






2bish
TAS, 815 posts
15 Jun 2020 8:08PM
Thumbs Up

Good one! Still toasty?

Regarding the beating heart fuel pump, I see that some recommend hanging them in a rubber webbing, even rigging up something woven up with occy rubber would work I guess, the intention is to completely isolate it from transferring vibration/sound to the hull. That along with some sound insulation should help. Also I saw that running the hard plastic nylon fuel hose inside a soft pipe insulation cover, so that no part of it touches anything hard, helps a lot too. I'm going to do all these, I don't want it noisy.

My unit arrived in the post today and I have the exhaust skin fitting already. Hopefully I'll get a chance this week to go and pull things apart on the boat to see where it'll best fit.




southace
SA, 4776 posts
15 Jun 2020 8:01PM
Thumbs Up

Select to expand quote
2bish said..
Good one! Still toasty?

Regarding the beating heart fuel pump, I see that some recommend hanging them in a rubber webbing, even rigging up something woven up with occy rubber would work I guess, the intention is to completely isolate it from transferring vibration/sound to the hull. That along with some sound insulation should help. Also I saw that running the hard plastic nylon fuel hose inside a soft pipe insulation cover, so that no part of it touches anything hard, helps a lot too. I'm going to do all these, I don't want it noisy.

My unit arrived in the post today and I have the exhaust skin fitting already. Hopefully I'll get a chance this week to go and pull things apart on the boat to see where it'll best fit.





Yes I'm toastie but threw the circuit breaker trying to refuel and start the heater at the same time. God it smoked up more than a indgionus smoking party once I Reset! I have run twin core 4mm tinned wire to aft cabin with positive / negative studs with the heater and fuel transfer pump on it , my circuit breakers are 30 amp so must of got there!
anyway she's running like trooper again since that smelly episode. I also have moved my D.V.k gas monitor from the Bilgie to the cabin where the hot air comes out. Very important.

Lazzz
NSW, 885 posts
15 Jun 2020 8:54PM
Thumbs Up

Select to expand quote
southace said..
God it smoked up more than a indgionus smoking party once I Reset!




I reckon it's unburned diesel laying in the low spot of your exhaust pipe - that's why you need a drain coil at the low point!!
I made my own out of copper pipe.

Nice job on the transfer pump - I just used an electric fuel pump off eBay!!





Select to expand quote
2bish said..

My unit arrived in the post today and I have the exhaust skin fitting already. Hopefully I'll get a chance this week to go and pull things apart on the boat to see where it'll best fit.






Have fun 2bish!!! :)

2bish
TAS, 815 posts
15 Jun 2020 9:05PM
Thumbs Up

Yikes! The heaters pull about 10 amps on start up I believe. What does your fuel transfer pump draw?

The DVK only monitors lpg gas doesn't it? what are you using to monitor carbon monoxide?

southace
SA, 4776 posts
15 Jun 2020 8:43PM
Thumbs Up

Select to expand quote
Lazzz said..

southace said..
God it smoked up more than a indgionus smoking party once I Reset!





I reckon it's unburned diesel laying in the low spot of your exhaust pipe - that's why you need a drain coil at the low point!!
I made my own out of copper pipe.

Nice job on the transfer pump - I just used an electric fuel pump off eBay!!






2bish said..

My unit arrived in the post today and I have the exhaust skin fitting already. Hopefully I'll get a chance this week to go and pull things apart on the boat to see where it'll best fit.







Have fun 2bish!!! :)


Your right about the unburnt diesel but na it was just the fact I blew the circuit breaker while start up. The drain is I thought just for condensation ? I don't care will take a life time to eat through the S/S exshust hose. Might stick a rubber bung in the outllet when not in use.

southace
SA, 4776 posts
15 Jun 2020 8:45PM
Thumbs Up

Select to expand quote
2bish said..
Yikes! The heaters pull about 10 amps on start up I believe. What does your fuel transfer pump draw?

The DVK only monitors lpg gas doesn't it? what are you using to monitor carbon monoxide?


My DVk does it all if I spray any pressure pack near the pick up the alarm goes off.

southace
SA, 4776 posts
15 Jun 2020 8:57PM
Thumbs Up

Select to expand quote
2bish said..
Yikes! The heaters pull about 10 amps on start up I believe. What does your fuel transfer pump draw?

The DVK only monitors lpg gas doesn't it? what are you using to monitor carbon monoxide?


Yes 10 amps on start up for about a minute. Goes through all the settings blows high then low eventually back to below 2 amps. My fuel transfer pump yes must use 10 amps maybe more but it's just for a minute Or so.

southace
SA, 4776 posts
16 Jun 2020 4:29AM
Thumbs Up

Select to expand quote
2bish said..
Yikes! The heaters pull about 10 amps on start up I believe. What does your fuel transfer pump draw?

The DVK only monitors lpg gas doesn't it? what are you using to monitor carbon monoxide?


You got me thinking there! Looks like a trip to Bunnings tomorrow!
www.bunnings.com.au/family-first-carbon-monoxide-alarm_p4210604

Lazzz
NSW, 885 posts
16 Jun 2020 7:55AM
Thumbs Up

Select to expand quote
2bish said..
what are you using to monitor carbon monoxide?


I have one from Bunnings as well.

southace
SA, 4776 posts
16 Jun 2020 4:32PM
Thumbs Up

Select to expand quote


I brought one from Bunnings today hasn't gone off yet!

I still would recomending instaling the unit in a separate compartment than your living area if possible.

2bish
TAS, 815 posts
16 Jun 2020 6:13PM
Thumbs Up

Apart from my anchor locker, everywhere else is open to the bilge and therefore living areas.

southace
SA, 4776 posts
16 Jun 2020 6:13PM
Thumbs Up

Select to expand quote
2bish said..
Apart from my anchor locker, everywhere else is open to the bilge and therefore living areas.

Ok , I see , a bloke here put one in a forward cabin he's not a liveaboard so not such a problem, I still think it's best to fit it in the aft section so all exhaust fumes travel from the transom. When I have northerlys I can smell the fumes in the south facing marina Berth, obviously perfect when on the pick. Keep us posted and don't be afraid to ask any questions.
regards
southace

Lazzz
NSW, 885 posts
16 Jun 2020 6:51PM
Thumbs Up

Select to expand quote
2bish said..
Apart from my anchor locker, everywhere else is open to the bilge and therefore living areas.


You'll have to keep it aft to keep the exhaust run as short as possible as well as the problems Southace mentions.

Mine is open to the bilge and causes no problems. As long as the exhaust has no leaks it shouldn't be an issue.

LooseChange
NSW, 2140 posts
16 Jun 2020 8:47PM
Thumbs Up

Select to expand quote
southace said..

2bish said..
Yikes! The heaters pull about 10 amps on start up I believe. What does your fuel transfer pump draw?

The DVK only monitors lpg gas doesn't it? what are you using to monitor carbon monoxide?



My DVk does it all if I spray any pressure pack near the pick up the alarm goes off.


You may be interested to know the that the propellant in pressure pack cans is butane, so of course your monitor will sing its t1ts off, it's the same stuff.

southace
SA, 4776 posts
16 Jun 2020 9:02PM
Thumbs Up

Select to expand quote
LooseChange said..

southace said..


2bish said..
Yikes! The heaters pull about 10 amps on start up I believe. What does your fuel transfer pump draw?

The DVK only monitors lpg gas doesn't it? what are you using to monitor carbon monoxide?




My DVk does it all if I spray any pressure pack near the pick up the alarm goes off.



You may be interested to know the that the propellant in pressure pack cans is butane, so of course your monitor will sing its t1ts off, it's the same stuff.


What are you saying ?

LooseChange
NSW, 2140 posts
17 Jun 2020 12:59AM
Thumbs Up

Select to expand quote
southace said..

LooseChange said..


southace said..
My DVk does it all if I spray any pressure pack near the pick up the alarm goes off.


You may be interested to know the that the propellant in pressure pack cans is butane, so of course your monitor will sing its t1ts off, it's the same stuff.



What are you saying ?


I'm saying that the gas in the pressure pack is butane so of course the gas monitor will sound the alarm if you squirt any pressure pack near it.

2bish
TAS, 815 posts
19 Jun 2020 6:05PM
Thumbs Up

I've bench tested my unit a few times over the past few days and all is working well. Southace, if your problem with your remote was pairing, watch this and it may help, I got mine paired up and working in 30 seconds.

- pairing instruction starts at 3:43.

I see what you mean about the beating heart of the fuel pump, I've got a spot in my insulated engine box that should quieten it down considerably.

I popped down to the boat today to grab my clamp meter so I can check the current draw, I want to make sure the supplied power loom is adequately sized. I had a quick look at a few spots where I thought I'd be running ducting. It's looking difficult actually, I intend to mount the unit in the back of the boat somewhere ( a lazurette or near the quadrant) and I'm having doubts about being able to run ducting beyond the aft cabin. The boat designer/manufacturer has squeezed every bit of usable space out of the interior and there's just not much room behind things to get a ducting run in. I may end up just having one outlet on the base of the aft cabin bunk pointing out the door, we'll see...

southace
SA, 4776 posts
20 Jun 2020 2:38AM
Thumbs Up

Select to expand quote
2bish said..
I've bench tested my unit a few times over the past few days and all is working well. Southace, if your problem with your remote was pairing, watch this and it may help, I got mine paired up and working in 30 seconds.
- pairing instruction starts at 3:43.

I see what you mean about the beating heart of the fuel pump, I've got a spot in my insulated engine box that should quieten it down considerably.

I popped down to the boat today to grab my clamp meter so I can check the current draw, I want to make sure the supplied power loom is adequately sized. I had a quick look at a few spots where I thought I'd be running ducting. It's looking difficult actually, I intend to mount the unit in the back of the boat somewhere ( a lazurette or near the quadrant) and I'm having doubts about being able to run ducting beyond the aft cabin. The boat designer/manufacturer has squeezed every bit of usable space out of the interior and there's just not much room behind things to get a ducting run in. I may end up just having one outlet on the base of the aft cabin bunk pointing out the door, we'll see...


I paried my remote shortly after posting here. I hardly use the Remote now anyway. I have my duct in the exact spot your your talking about works fine but not sure how the crew will go sleeping in that cabin while the heater is running.
my heater runs at 2kw low setting and draws 1.6 to 1.8 amps.

2bish
TAS, 815 posts
20 Jun 2020 4:28PM
Thumbs Up

Select to expand quote
southace said..

2bish said..
I've bench tested my unit a few times over the past few days and all is working well. Southace, if your problem with your remote was pairing, watch this and it may help, I got mine paired up and working in 30 seconds.
- pairing instruction starts at 3:43.

I see what you mean about the beating heart of the fuel pump, I've got a spot in my insulated engine box that should quieten it down considerably.

I popped down to the boat today to grab my clamp meter so I can check the current draw, I want to make sure the supplied power loom is adequately sized. I had a quick look at a few spots where I thought I'd be running ducting. It's looking difficult actually, I intend to mount the unit in the back of the boat somewhere ( a lazurette or near the quadrant) and I'm having doubts about being able to run ducting beyond the aft cabin. The boat designer/manufacturer has squeezed every bit of usable space out of the interior and there's just not much room behind things to get a ducting run in. I may end up just having one outlet on the base of the aft cabin bunk pointing out the door, we'll see...



I paried my remote shortly after posting here. I hardly use the Remote now anyway. I have my duct in the exact spot your your talking about works fine but not sure how the crew will go sleeping in that cabin while the heater is running.
my heater runs at 2kw low setting and draws 1.6 to 1.8 amps.


Ok good one , glad you got that sorted. I'll probably use my remote because we mostly don't sleep with a heater on and it'll be nice to fire it up before we get out of bed. You may find that you use it more like that in your shoulder periods too, when it's not really cold enough to warrant having it on overnight, but nice to fire it up over breakfast?

I did my final bench tests this arvo. Using the clamp meter, my 5kw unit seems to draw up around 8 amps on start up (and shut down). Lowest heat setting - 1.6 hz draws only half an amp and the highest setting - 5.5 hz is pulling 2 amps.

I'm pretty impressed by the simplicity of these things and surprised at how clean they run. Can't wait to get it installed and working.

southace
SA, 4776 posts
20 Jun 2020 4:50PM
Thumbs Up

It's worth the effort to make a mounting frame like I did. You can see the duct outlet and control panel mounted in the aft cabin.











2bish
TAS, 815 posts
21 Jun 2020 11:05AM
Thumbs Up

Ah yes that's exactly what I'd imagined, very helpful to see your vent set up, thanks.

And yes I will make up some kind of frame depending on the eventual mounting location. Very clever use of those Bunnings bent ply brackets there! I brought a couple of small ones for my shed the other day (I've been insulating and lining it out during my business's hibernation) and I was surprised at how rigid they are.



Subscribe
Reply

Forums > Sailing General